      Hi All,

      I’m trying to put together some control logic to both cool and heat using a dead band. Currently I’m using a CMP block for cooling, this works really well. Now need to add heating to this. I was think about using two relay blocks but I’m sure there is a better way.

      Thoughts?

      Cheers

      Mike

      1 Reply Last reply Reply Quote 0
      • jaroslav_sobotaJ
        jaroslav_sobota
        last edited by

        Hi Mike,
        how about using the PWM block?

        If u=-1, then UP will be ON and you can use it for heating. If u=0 then both outputs are off. And if u=-1 then DN will be ON and you can use it for cooling.

        The PWM:offtime parameter defines the minimum delay between heating and cooling phases.

        Let me know.

        Kind regards
        Jaroslav

        1 Reply Last reply Reply Quote 0
        • M
          MikeyH
          last edited by

          Hi Jaroslav,

          What would work but wouldn't I then have to use a PIDU block (or similar) for the main process control? I don't need the accuracy of a PID controller.

          This is my current cooling solution.

          0_1571428686770_70df882c-0931-4f10-bb0e-974a55c504f4-image.png

          I'm guessing keeping it simple now I require heating isn't so easy 🙂 Other people need use this after myself so I trying to not over complicate it. But if I need to then I will, no problem.

          Cheers

          Mike

          1 Reply Last reply Reply Quote 0
          • jaroslav_sobotaJ
            jaroslav_sobota
            last edited by

            Hi Mike,
            I see. In that case the simplest approach is to use the TSE block (three state element), which moreorless combines two comparators with hysteresis.
            0_1571645853248_rexygen_tse_cooling_heating.png

            Kind regards
            Jaroslav