    Output to Analoge output

    REXYGEN Studio
    2
    2
    271
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • M
      martijnperdaan
      last edited by

      what is wrong here it is a normal CNR block with the value 1680 I place it outside the subsystem block directly on the output Extentons__xS51_1_AO1 I measure 4.2 volts I place the CNR block in the subsystem block it gives no output to the output Extentons__xS51_1_AO1

      scan.png

      1 Reply Last reply Reply Quote 0
      • cechuratC
        cechurat
        last edited by

        Hi Martijn,

        please, check the TagVisibility parameter of Goto flag - if it is set to "local" it is not visible to the MB driver. Also check the output of REXYGEN Compiler which will tell you details about wrong setup of flags.

        Kind regards,
        Tomas

        1 Reply Last reply Reply Quote 0