      Hello I have a problem with analog temperature measurement. The value fluctuates too much, see image Tmp.png. How to stabilize this value?
      Thank you Michal
      Tmp.png
      mcp3208.png

      1 Reply Last reply Reply Quote 1
      • P
        pancirm
        last edited by

        So I solved it with the AVG block, but I had to play with the tick settings of the whole algorithm, the number of samples and the range of fluctuating values over time.

        cechuratC 1 Reply Last reply Reply Quote 1
        • cechuratC
          cechurat @pancirm
          last edited by

          @pancirm Hi Michal,

          Thanks for your posts. There is no one-shot solution for general filtering applications so playing around with AVG function block would be the approach I would recommend. There are also some filters which can be used - low-pass, band-pass, and spike.

          Kind Regards,
          Tomas