Output to Analoge output
-
what is wrong here it is a normal CNR block with the value 1680 I place it outside the subsystem block directly on the output Extentons__xS51_1_AO1 I measure 4.2 volts I place the CNR block in the subsystem block it gives no output to the output Extentons__xS51_1_AO1
-
Hi Martijn,
please, check the TagVisibility parameter of Goto flag - if it is set to "local" it is not visible to the MB driver. Also check the output of REXYGEN Compiler which will tell you details about wrong setup of flags.
Kind regards,
Tomas