      Scoobsalamander
      last edited by

      I"m trying to communicate with a Beckhoff BK9000 bus coupler and to reset the watchdog timer I need to send consecutively the values 0xBECF and 0xAFFE to a single register.

      I only want to send this reset command when the watchdog timer elapsed due to some problem....

      I'm not sure if this is possible with Rexygen......

      1 Reply Last reply Reply Quote 0
      • cechuratC
        cechurat
        last edited by

        Hi Scoobsalamander,

        thanks for your question. If I understand correctly the solution can look like:

        0_1560321840892_911a57a2-c6a3-4ebd-8885-c9f09d5ac2d7-image.png

        Sample source file: Beckhoff_resetWatchdog.mdl

        Hope it helps.

        Cheers, Tomas

        1 Reply Last reply Reply Quote 0
        • S
          Scoobsalamander
          last edited by

          Hi Tomas,

          Thanks, this is indeed a working solution. I only needed to slow down the messages to 1 per second, which is still fine.

          1 Reply Last reply Reply Quote 0
          • cechuratC
            cechurat
            last edited by

            Hi Scoobsalamander,

            glad I could help. You are right, I didn't take to count the timing. Good luck with your project!

            Cheers, Tomas

            1 Reply Last reply Reply Quote 0